UDT CLI polling for Layer 2 and Layer 3
This article explains how to enable CLI Polling for UDT Layer 2/3, what to expect per device type, and how to troubleshoot common issues. Some devices — Cisco Nexus switches (5K/7K/9K), Palo Alto firewalls, and Cisco ASA firewalls — do not expose full Layer 2/3 (IP-to-MAC/ARP) data via SNMP. For these devices, User Device Tracker (UDT) supports polling Layer 3 data over CLI (SSH) instead of, or in addition to, SNMP.
UDT normally collects Layer 2 (MAC address) and Layer 3 (IP address / ARP) data via SNMP. Certain device families restrict or do not expose the SNMP MIBs UDT needs for Layer 3 (ipNetToMediaTable / ipNetToPhysicalTable). CLI-based polling may be used as a supported workaround.
CLI polling behavior differs by device type:
Cisco Nexus (5K/7K/9K): CLI polling supplies Layer 3 data only. Despite documentation wording suggesting both Layer 2 and Layer 3 are polled via CLI, Layer 2 (MAC address) data for Nexus devices is still collected via SNMP. Only Layer 3 uses CLI.
Palo Alto firewalls: CLI polling supplies both Layer 2 and Layer 3 data, since SNMP MIB support on Palo Alto is limited (ARP/MAC tables are not exposed via supported SNMP MIBs).
Cisco ASA firewalls: CLI polling is scoped to the ARP table only (
show arp), used to fill in Layer 3 data that SNMP cannot provide. ASA devices do not have Layer 2 forwarding data to poll.
CLI polling uses the SolarWinds CLI Client Orion package and communicates over SSH (port 22 by default; unencrypted Telnet on port 23 is supported only if explicitly enabled).
Enable CLI Polling for Layer 3
Add the device to UDT as a standard SNMP node first (SNMP credentials remain required as a base).
Open Edit Node Properties (or use the last step of the Add Node wizard) and locate the CLI Polling Settings section.
Select Enable CLI Polling and provide:
Username and password for CLI login.
Enable password — required to reach privileged EXEC mode on Cisco devices (Nexus, ASA). This field is optional for Palo Alto, since Palo Alto does not support "Enable mode" commands.
For Palo Alto devices that present an Authorization Statement prompt at login, set Use Keyboard Interactive Authentication to Yes; otherwise CLI access will be denied.
Click Test to validate the credentials, then Submit.
UDT schedules a Layer 3 CLI job for the node. Data appears in the Port Details resource on the Node Details page once the job completes successfully.
Note: Credential changes are picked up by the collector approximately every 30 seconds via PubSub. Poll Now / Rediscover Now do not speed this up.
Verify the Layer 3 CLI job
Go to Settings > All Settings > UDT Settings > View UDT Job Status and confirm a Layer 3 job exists for the node and completes with a Success status.
Run the UDT Compatibility Checker against the node using the Layer 3 target to confirm the device returns ARP/IP-to-MAC data over the selected protocol (SNMP or CLI). If the device doesn't support the required SNMP objects at all, CLI is the only way to retrieve Layer 3 data.
For Nexus nodes, if Layer 2 data is missing while Layer 3 (via CLI) works, this is expected — Layer 2 for Nexus is polled via SNMP, not CLI. Investigate the SNMP/Layer 2 job separately rather than the CLI configuration.
Troubleshoot CLI polling failures
Enable CLI session tracing to capture the raw CLI conversation with the device:
Go to Settings > All Settings > CLI Settings, select Enable Session Tracing, and Submit.
Reproduce the issue, then collect trace files from
C:\ProgramData\SolarWinds\Logs\Orion\CLI\Session-Trace(named using the device's IP address). -
Disable session tracing and delete trace files afterward to avoid unnecessary log growth.
Set UDT Business Layer and UDT Jobs logging to Debug, then rerun the Layer 3 job (Poll Now from the UDT Job Status page) to capture detailed job processing logs.
Check for Enable password misconfiguration on Nexus/Cisco devices — a saved Enable password that isn't actually required (or incorrect Enable mode credentials) is a common cause of failed CLI polling on Nexus.
Check job timeouts — if the device responds slowly (visible via long durations in the UDT Compatibility Checker), increase the Layer 2/Layer 3 job timeout on the Advanced Settings page. In at least one case, increasing the timeout from 45 to 100 minutes resolved persistent Layer 3 polling failures on slow-responding Nexus nodes.